I have a 30 Amp Dryer connected to a subpannel. The Dryer receptical has 10 guage wire. It has a black wire, a white wire taped red and a bare ground wire. This iis for a 3-prong plug. Is this considered and an ungrounded receptical and should not be wired to a subpannel, but only the main. Is that correct? As the bare wire comes into the subpannel it is connected to the ground bar and not the neutral bar. Is that correct or should it be on the neutral bar? Seems to me that this configuration has created a parallel ground as the bare wire is acting as the grounded conductor (neutral) and not a grounding conductor. Is that correct? I am confident that under current code, if the dyer was being installed new, would be to run 10-3 with ground to a 4 wire receptical; and then, in the subpannel, keep the neutral and ground separated. I dont think configuration should be left as is as it is not only up to code but should never have been run this way to begin with?