6/3 UF in a clamp connector

Status
Not open for further replies.

Jack Hass

Member
Location
NY
Subpanel has two 6/3 NM UF cables, one in, one out. Anything wrong with putting two 6/3 NM UF cables in a 2" clamp connector?

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yup, I will bet that it's not listed for two cables. If you can find a connector listed for 2-6/3 cables then you can use it.
 

peter d

Senior Member
Location
New England
I wouldn't worry about it too much as long as the connector holds the cables tightly. I would prefer to use the flat SEU style connectors for this myself.
 