from this study book photo attached, the cable going to the second receptacle, (not
switch controlled). is it practical to route it through the switch box?
Grounded conductor not required at a switch controlling a receptacle outlet.If you want to do it that way you would need a 3 wire cable between the switched receptacle and the switch since the switch location does not have a neutral.
Grounded conductor not required at a switch controlling a receptacle outlet.
If one wanted to run through the switch box to get to the end outlet in question would be more practical to do so with 3 wire (with ground) cable, but would still be acceptable to run 2-two wire cables to the switch box. One has to pay more attention to box fill the more conductors you run to it.
I think that almost all electricians would choose to run one 3 wire cable in lieu of two 2 wire cables. Unless you only had 2 wire cable running two of them would be kind of silly.
Also depends a little on actual arrangement of things. In reality that "end receptacle" may not be practical to have it's supply run through/near the switch at all. Laying it all out like they did in that image for the sake of showing connections just makes it read a little like a wiring diagram IMO.I think that almost all electricians would choose to run one 3 wire cable in lieu of two 2 wire cables. Unless you only had 2 wire cable running two of them would be kind of silly.