ritelec

Senior Member
Location
Jersey
over 250 volt,

For boxes rated for bonding with eccentric and concentric ko's, no grounding bushings are required...
I'm assuming standard lock nuts are acceptable.... correct?

For other enclosures and boxes not rated,when there are concentric and eccentrics a bonding jumper (grounding bushing) is required.
If all the concentric or eccentric rings are removed, is a standard lock nut to the box acceptable, or does it have to be a grounding locknut ?

thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
over 250 volt,

For boxes rated for bonding with eccentric and concentric ko's, no grounding bushings are required...
I'm assuming standard lock nuts are acceptable.... correct?
IMO, yes

For other enclosures and boxes not rated,when there are concentric and eccentrics a bonding jumper (grounding bushing) is required.
If all the concentric or eccentric rings are removed, is a standard lock nut to the box acceptable, or does it have to be a grounding locknut ?
again, IMO, standard locknuts are acceptable.

thank you
(above based on non-service conductors)
 

ritelec

Senior Member
Location
Jersey
ok great..........


not that I'll be working with that voltage soon, but was thinking about it recently..



Thank you !!!
 