hmmm, for what purpose are you doing this? ground rods sounds like bonding, which is usually #8 or bigger bare copper.
is this your 1st use of wire?
my inclination is to say no under NEC, but maybe yes if its the right color and used as a tracer wire not connected??
what color do you think it should be?
The insulation type is basically not relevant as a GEC can be bare. What is relevant is whether you are talking about a copper or aluminum conductor. Aluminum conductors cannot be in contact with bare earth and IIRC must be terminated like 18" above ground.
as a tracer? red for electric, blue for water, yellow for gas.what color do you think it should be?
No, he meant the complete GEC color
as a tracer? red for electric, blue for water, yellow for gas.
Is thwn ok to run to ground rods i do not see where thwn can be indirect contact with the earth soil.
can i bury a 2 CCC cable marked for direct burial along with a #6 bare copper out to a sub panel 100ft away, and, use that bare copper for EGC?Conductors used for direct-burial shall be of a type identified for the use. Whatever that means. So, I would say that THWN looks good to me.
This thread is not about an EGC.can i bury a 2 CCC cable marked for direct burial along with a #6 bare copper out to a sub panel 100ft away, and, use that bare copper for EGC?
exactly the statement i was waiting for, i just had to lead someThis thread is not about an EGC.
Roger
And none of that has anything to do with the OP's question so if you want to talk about something else start a new thread.exactly the statement i was waiting for, i just had to lead some
right, so it doesnt really matter
250.62 #8 copper #6 aluminum min
if it is very wet salty soil, like ocean front property, i would perhaps choose direct burial rated. southwire makes #8 copper tracer in 30v and 600v, way cheaper than other direct burial rated wire.
And back to the GEC discussion at hand, what makes you think it should be green?i guess the color should be green?
And back to the GEC discussion at hand, what makes you think it should be green?
Roger
No it doesn't, you need to read the definition of Equipment Grounding Conductor verses Grounding Electrode Conductor.it does have everything to do with OP's Q. did you read the Q ? THWN is a protector, good enough fro 250, etc.
doesnt 250.62 say "grounding electrode conductor" ? or is it written in chinese and my translation is off?No it doesn't, you need to read the definition of Equipment Grounding Conductor verses Grounding Electrode Conductor.
Roger
250.26 has nothing to do with the conductor the OP is asking about.doesnt 250.26 say "grounding electrode conductor" ? or is it written in chinese and my translation is off?
250.62 does have everything to do with GEC? no?250.26 has nothing to do with the conductor the OP is asking about.
With that said, we're not going to play your games, we are talking about the GEC and if you want talk about something else, I'll say it again, start another thread.
Roger
Yes, but you edited after my post, you originally stated 250.26.250.62 does have everything to do with GEC? no?
250.62 does have everything to do with GEC? no?