Rcr29kh1

Member
Location
Burtonsville, MD
408.41 Says each grounded conductor shall terminate in an individual terminal that is not used for another conductor
EXCEPTION: Grounded conductors of circuits with "parallel conductors" shall be permitted to terminate in a single terminal if the terminal is identified for more than one conductor.

what about a panel connection for a 200% neutral? I don't think a 200% neutral is to be considered as a parallel condition

Thoughts?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Are you paralleling the neutral? If so it is parallel, i.e electrically joined at both ends. If it is a single conductor then you need a lug big enough for that conductor.
 