408.41 Says each grounded conductor shall terminate in an individual terminal that is not used for another conductor
EXCEPTION: Grounded conductors of circuits with "parallel conductors" shall be permitted to terminate in a single terminal if the terminal is identified for more than one conductor.
what about a panel connection for a 200% neutral? I don't think a 200% neutral is to be considered as a parallel condition
Thoughts?