MC Cable Used Outdoors

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • jumper
    replied
    Originally posted by kwired View Post
    If they have the "stop" they are not intended for NM cable, they are intended for AC, MC and even flexible metal conduit.
    And some are listed for NM also.

    http://www.aimedia.co/media/catalog-pages/E-13-3.pdf

    Leave a comment:


  • kwired
    replied
    Originally posted by Andy Delle View Post
    I thought Romex connectors were compliant for MC as long as they have the "stop" built in to hold the bushing in place?
    If they have the "stop" they are not intended for NM cable, they are intended for AC, MC and even flexible metal conduit.

    Leave a comment:


  • LarryFine
    replied
    Originally posted by Andy Delle View Post
    I thought Romex connectors were compliant for MC as long as they have the "stop" built in to hold the bushing in place?
    Consider that MC does not require bushings.

    Leave a comment:


  • Andy Delle
    replied
    Originally posted by jumper View Post
    Not compliant: no outer jacket, wrong connectors, and not secured properly.
    I thought Romex connectors were compliant for MC as long as they have the "stop" built in to hold the bushing in place?

    Leave a comment:


  • kwired
    replied
    single whip of liquidtight (metallic or NM, pick your poision) would look better then two whips down to the timer. Also why not run it out of the end hub on the box instead of out of the cover?

    Leave a comment:


  • gadfly56
    replied
    Originally posted by Jsim4109 View Post
    Those (3) boxes originally had photocells for controlling the common space lighting and outdoor lighting for the multi-occupancy residence. The building occupants didn't like the lights on all night long so the builder had someone (probably the landscaper) install the outdoor rated time clock and configure that wiring so the lights shut off at a certain time. These boxes are under the floor of the residence above. The weather does not directly rain in them so i would assume this is a damp location not wet?

    So other that ugly as heck, i succumb to the fact that the wiring is code compliant but are the connectors UL listed for damp locations?
    Is the time clock box possibly exposed to rain or wind-driven or not? Are the WP boxes possibly exposed to wind-driven rain or not?

    Leave a comment:


  • Jsim4109
    replied
    Those (3) boxes originally had photocells for controlling the common space lighting and outdoor lighting for the multi-occupancy residence. The building occupants didn't like the lights on all night long so the builder had someone (probably the landscaper) install the outdoor rated time clock and configure that wiring so the lights shut off at a certain time. These boxes are under the floor of the residence above. The weather does not directly rain in them so i would assume this is a damp location not wet?

    So other that ugly as heck, i succumb to the fact that the wiring is code compliant but are the connectors UL listed for damp locations?

    Leave a comment:


  • kwired
    replied
    Originally posted by MAC702 View Post
    Whoever originally put up the WP boxes probably thought they were needed...

    If the MC isn't allowed, neither is that timer enclosure.
    Without a little closer examination....that possibly is a outdoor rated timer enclosure, they don't look much different from afar or at wrong angles.

    Leave a comment:


  • jumper
    replied
    Originally posted by MAC702 View Post
    Well, so far, I see no reason to think they wouldn't have grounded everything. MC includes an insulated EGC.
    Yep.

    Leave a comment:


  • MAC702
    replied
    Originally posted by IK77 View Post
    Grounding????...
    Well, so far, I see no reason to think they wouldn't have grounded everything. MC includes an insulated EGC.

    Leave a comment:


  • IK77
    replied
    Grounding????


    Sent from my iPhone using Tapatalk

    Leave a comment:


  • hbiss
    replied
    Originally posted by mike7330 View Post
    Is that really MC?
    I can see the time clock is a pvc / plastic enclosure
    How is the clock grounded? Provisions in time clock for grounding? Bonding bushings?
    Is the AC / MC even grounded in the bell boxes?
    I think the use of AC/MC is only one issue here amid probably a half dozen other violations that are just as bad. Obvious DIY/hacker job that all needs to be torn out.

    -Hal

    Leave a comment:


  • jumper
    replied
    Originally posted by Strathead View Post
    True we still have the original issue of wet location damp location that hasn't been truly answered.
    Prolly because that is an inspector's call. Our opinion is worth didley.

    Leave a comment:


  • mike7330
    replied
    Grounding?

    Is that really MC?
    I can see the time clock is a pvc / plastic enclosure
    How is the clock grounded? Provisions in time clock for grounding? Bonding bushings?
    Is the AC / MC even grounded in the bell boxes?

    Leave a comment:


  • MAC702
    replied
    Whoever originally put up the WP boxes probably thought they were needed...

    If the MC isn't allowed, neither is that timer enclosure.

    Leave a comment: