I got a call from a customer this past week. He said he was having issues with the electrical in his summer cottage. I went there today to check it out. I checked the voltage on the 2 main breaker lugs and got 220V. When I tested leg to ECG i got 236V on 1 leg and around 60V on the other leg. I turned all the breakers off and recheck voltage and got a perfect 110/110 on each leg. Only when I apply a load does the voltage seem to get screwed up. I have seen this happen when a neutral is lost from PoCo. How would I be able to tell if the problem is on the utility side of the equipment?