Cord in Conduit

Status
Not open for further replies.

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
I noticed in a few supermarkets they have gray cord coming out of conduit (rmc/emt) at the ceiling with a cord grip / strain relief on the end, conduit appears to look like a chase through the ceiling tile. No cord above ceiling, but how then is the cord being terminated in jbox?
 

tank728

Senior Member
Location
New Jersey
Occupation
Electrician
They may be using the conduit as a sleeve to comply with article 400.12 (or .10 ). Where uses not permitted states flexible cords shall not be above a suspended ceiling.

The way I have seen it done is the cord terminates in a junction box through the conduit acting as a sleeve
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There very well may be a Section I've missed but it seems 400.14 for industrial establishments is the only place that is allowed.
 