I moved this to its own thread [MENTION=159869]Tim Dossett[/MENTION]

Afaik, the limitation is for overhead conductors but if it is closer than 5' it must be bonded. I probably would keep it at least 6' away but I am not sure that is required. Check with the authority having jurisdiction or you may have a fight on your hand.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
It looks like this falls under "other outlets" which need to be 10' or 3.0m away from the inside wall of the pool.
 