Hello everyone, today I had a phase UW (T1&T3) short fault on an ab powerflex 4m drive that powers a 1hp 3ph 460v induction motor. When I reset the drive the fault code comes right back up after receiving a run signal. I took the leads off the drive and tested resistance between the 3 leads that were still connected to the motor each lead read 13.8 ohms amongst each other (T1 to T2, T1 to T3, T2 to T3). Then I megged each lead to ground at 1000v each reading was infinite, 1Mohm on my tester. Assuming the motor was ok, I went ahead and replaced the drive, which we have numerous spares. Same problem. Swapped T1 and T2 and tried to run and the drive faulted out with a VW (T2&T3) short. Disconnected motor from gearbox and spun both shafts by hand and everything spun freely including the load. Then tried to run motor while disconnected, same problem. I unwired the motor and temporarily wired in a spare and it ran fine without fault. After assisting the machinist with the install of the new motor I looked up specs on the motor and resistance from line to line should be 3.5 ohms, but I was getting 13.8 ohms from line to line, however T1 to T4&T7, T2 to T5&T8, etc all read around 3.5ohms. As I have only been an industrial electrician for a little over 2 years this is leaving me puzzled. Even our senior electrician was lost. Any tips, suggestions would be greatly appreciated. The motor is still on my bench and I’d like to try to troubleshoot it more. Thanks in advance