What prevents a 30 amp 120 volt circuit to be broken down to (2) 15 amp 120 volt circuits at a 2 pole breaker disconnect?
It could even serve two 20-A circuits from such, assuming load calcs allow it.
What prevents a 30 amp 120 volt circuit to be broken down to (2) 15 amp 120 volt circuits at a 2 pole breaker disconnect?
If you had 42 circuits and total load never exceeded 30 amps, it doesn't matter if one load is 20 amps and the others never put it over 30. Can even have several 20 amp loads, if arranged that they never run simultaneously.As alluded by others:
The 30A cb does have to be able to support the end load.
I don't see any code reason why you couldn't have a panel full (42) of 15A CBs. The loads would have to be .7A or less, non-continuous.
pretty piss poor design - but meets code
It was always taught the smallest circuit(feeder) that could be broken down to a subpanel is a 30A 120/240V feed. It was grilled into our heads over the years that it became practice. I am not finding it in the Code. So what you are saying is there is nothing wrong with taking an existing 30 amp 120v ciricuit into a 2 circuit breaker panel, using a wirenut to feed the same phase to both hot lugs, and leaving the panel with (2) 15 amp 120 volt circuits? I believe you said that was fine but like I said it was not taught that way in our area. Thanks.