Need to make sure I'm not missing something.
I would like to punch a 3-1/2 in hole about 20 inches from the bottom of a N3R 400 amp disconnect to install a short piece of conduit from the meter base mounted next to it.
The only reference I can find covering this non-factory entrance is:
312.2 states " For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall have fittings listed for wet locations"
Is there any section I have missed that would not allow this?
Dj