Need to step up from 120/208v to 120/240v

Status
Not open for further replies.

Dean Champ

New User
Location
Austin, TX, USA
I have several jobs in downtown Austin, Texas. Austin Energy only provides 120/208v in the downtown area. I need 120/240v power. Would use of a buck boost transformer be what I need? If so, what type would you recommend?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have several jobs in downtown Austin, Texas. Austin Energy only provides 120/208v in the downtown area. I need 120/240v power. Would use of a buck boost transformer be what I need? If so, what type would you recommend?

3 phase or single phase for the 120/240?
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
What you need is what is required.

The BB xfrmers do work in many cases, but what do the loads require (total amps, 1ph, 3ph 3wire, 3ph 4wire)??
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have several jobs in downtown Austin, Texas. Austin Energy only provides 120/208v in the downtown area. I need 120/240v power. Would use of a buck boost transformer be what I need? If so, what type would you recommend?

It seems to me that a buck boost won't do it. The phase voltages are already 120V from the neutral while they are only 208V apart. It seems to me that if you boost the phase voltages to 240V apart they will be farther than 120V away from the neutral.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
It seems to me that a buck boost won't do it. The phase voltages are already 120V from the neutral while they are only 208V apart. It seems to me that if you boost the phase voltages to 240V apart they will be farther than 120V away from the neutral.
That's true. One ends up with 139/240

We will have to wait for the OP to tell us if the requirement is 120/240 single phase
or
240/120 center tapped Delta
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It seems to me that a buck boost won't do it. The phase voltages are already 120V from the neutral while they are only 208V apart. It seems to me that if you boost the phase voltages to 240V apart they will be farther than 120V away from the neutral.
That doesn't matter to loads that don't use the neutral, and also applies to deltas with derived neutrals.
 

mpoulton

Senior Member
Location
Phoenix, AZ, USA
Assuming this is all single phase (i.e. you need to make 120/240 split-phase, not high-leg delta) then you can't do it with buck-boost. You need a transformer with a 208V primary and 120/240V secondary. The reason is that you must derive your own new neutral, since your service is actually two phases of a 3ph system and therefore do not have a 180-degree phase relationship compared to the service neutral.
 

kwired

Electron manager
Location
NE Nebraska
It seems to me that a buck boost won't do it. The phase voltages are already 120V from the neutral while they are only 208V apart. It seems to me that if you boost the phase voltages to 240V apart they will be farther than 120V away from the neutral.
depends on whether you use buck boost in a wye configuration or a delta configuration. Most common would be an open delta configuration, in that arrangement one of your supply leads is still common to the output leads and is still 120 volts to the supply neutral. You would most likely use this for boosting voltage to an individual utilization equipment that primarily needs 240 volts three phase, though if it also has limited 120 volt single phase it could be connected to that "common" lead. I'd think it would be best in most cases to still utilize 208/120 source to supply your general 120 volt loads, and whatever loads you can that will work @ 208 (single or three phase) and then put whatever needs to be 240 on buck boost or even separately derived system - depending on what analysis of the situation.

Keep in mind a 208 system that typically runs on high side (like about 215 volts) isn't all that much lower than a 240 volt system that is running near the low end of general accepted tolerance range.

240 less 5% is 228, 208 plus 5% is 218.

That doesn't matter to loads that don't use the neutral, and also applies to deltas with derived neutrals.

There is another thread, fairly current about buck-boost and 208 to 240 volts, with pretty good discussion on wye vs open delta configuration of the buck-boost transformer(s).
 