Again, thank you everyone for the help you are providing me. If you will, a few more questions:
1. Is there any code that dictates what wire is required for different amp circuits?
The NEC
2. Is there any code that limits the length of wire on different circuits?
No, other than Local requirements.. It is a design issue.
3. Is there any code that limits the number of outlets on a circuit?
No, other than Local requirements.. It is a design issue.
4. At what point is it reasonable to say "that is too much voltage drop"?
Eventually the equipment will not perform as intended. The manufacturer may have min/max requirements and those should be adhered to.
5. What issues happen when we have too much voltage drop?"
The smoke gets out of motors, light flicker is excessive, items do not operate as intended.
6. Is voltage drop an issue with DC devices? Is so - at what voltage level?
Yes, again, that will depend on the sensitivity of the equipment.
7. Does it make sense to test voltage drop on a circuit using 100% load or should 80% be use?"
Use 100% if you expect that to be the norm, There are "rule of thumb" like "increase a wire size for every hundred feet of branch circuit. A residential branch circuit may never see 30% load for any length of time, let alone 80-100%
8. Have there been any studies done on voltage drop that may help explain why everyone is saying this isn't something to be concerned about?