Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I have a set of drawings where the engineer is putting a 480V Switchboard facing a fire alarm terminal cabinet and a fire alarm control panel. The engineer states that the working clearance between the equipment will be 42", so I'm guessing that it's not 48" because of the voltage of the fire alarm equipment. Is the engineer correct if that is the reason?
110.26 (A)(1)
Condition 2 at 480V grounded parts one side is 42"
Condition 3 at 480V live parts on both sides is 48"
110.26 (A)(1)
Condition 2 at 480V grounded parts one side is 42"
Condition 3 at 480V live parts on both sides is 48"