680.42 (B) talks about not needing the equipotential bonding around the perimeter if all 4 requirements are met..
Am I reading this correctly, - (4) rim has to be 28" above perimeter surfaces up to 30" away from the tub.
The question, if I install a equipotential perimeter bond around the tub,
could I build a brick wall right next to the tub 10' High if I wanted??
Thank you