Forgive me if this has been discussed before. I couldn't find it in a search.

I am in a healthcare setting and we are required to transfer power within 10 seconds which is tested monthly and documented. We can't always meet that due to our closed transition switches. Is there any exceptions to the 10 second rule that would allow for the syncing of the two power sources during testing? We could open normal power and will meet the time. However, there are many instances where it is not practical to do so.

When we go over, the timing is generally around 11-18 seconds. Any assistance would be appreciated. Thank you
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Forgive me if this has been discussed before. I couldn't find it in a search.

I am in a healthcare setting and we are required to transfer power within 10 seconds which is tested monthly and documented. We can't always meet that due to our closed transition switches. Is there any exceptions to the 10 second rule that would allow for the syncing of the two power sources during testing? We could open normal power and will meet the time. However, there are many instances where it is not practical to do so.

When we go over, the timing is generally around 11-18 seconds. Any assistance would be appreciated. Thank you

Out of curiosity I'm guessing you have just 1 genset or if you have multiple in parallel any 1 can carry the 10 second loads and thus be compliant except when doing testing with the closed transition with the POCO?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The 10 second rule only applies on actual loss of normal power, I don't think there is any way to test that if the transfer switch is a closed transition switch and both sources are available.
517.32(B) The life safety and critical branches shall be installed and connected to the alternate power source specified in 517.30(A) and (B) so that all functions specified herein for the life safety and critical branches are automatically restored to operation within 10 seconds after interruption of the normal source. [99:6.4.3.1]
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
ATS Meeting the 10 sec rule in health care environments

ATS Meeting the 10 sec rule in health care environments

Forgive me if this has been discussed before. I couldn't find it in a search.

I am in a healthcare setting and we are required to transfer power within 10 seconds which is tested monthly and documented. We can't always meet that due to our closed transition switches. Is there any exceptions to the 10 second rule that would allow for the syncing of the two power sources during testing? We could open normal power and will meet the time. However, there are many instances where it is not practical to do so.

When we go over, the timing is generally around 11-18 seconds. Any assistance would be appreciated. Thank you

First of all, the problem you are experiencing has nothing to do with you having closed transition switches. Whether closed transition (make-before-break) or open transition (break-before-make) design, ATS's employ a feature called an in-phase monitor which is nothing more than a sync check circuit to only allow transfer when both sources are within a certain sync threshold (usually within 10 electrical degrees.) This occurs when the test is performed from the test switch on the controller, what we call a hot bus - hot-bus test. or during a re-transfer after a power failure.
From what you are describing, when you test from the test switch you cannot meet the 10 sec requirement. This indicate that there is an unusually long sync time before transfer. We find the most common reason for this is that the genset frequency is set either too close or too far away from the utility: 60.00HZ. GE-Zenith recommends a setting of 60.10HZ. We like to see it set at 60.20HZ to allow for speed drift.
When you test by opening the normal source breaker (which no hospital likes to do, but simulates a real power failure) you meet the 10 second rule. In this type of test, we call a dead bus - hot bus test, your closed transition ATS reverts to a delayed transition ATS with a faster transfer time since there is no sync time in the equation.
I would recommend calling in your genset vendor to adjust the frequency to 60.20HZ for a faster sync time. Most younger techs aren't aware of this and are prone to setting it dead on 60.00HZ. The other problem is that most gensets come from the factory set at 60.00HZ and either requires a laptop program to make changes or the tech ordering and installing an accessory panel to correct the problem as in the case of Kohler.
I have attached files from 2 previous jobs that may also help to explain the situation. Good luck.
 

Attachments

  • ATS Utility Frequency variation problem_1.doc
    27.5 KB · Views: 8
Last edited:

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Second attached file

Second attached file

Sorry
See 2nd file
 

Attachments

  • ATS unusually long transfer times.doc
    29.5 KB · Views: 4

Microwatt

Senior Member
Location
North Dakota
We do similar testing for a healthcare entity and had a similar issue. What we are now permitted to do is time from when the test switch is activated to the time the emergency source becomes available to the ATS. You might want to run this past the local Department of Health first.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
We do similar testing for a healthcare entity and had a similar issue. What we are now permitted to do is time from when the test switch is activated to the time the emergency source becomes available to the ATS. You might want to run this past the local Department of Health first.

Yes but that does not comply with the code wording stated in post #3 by Don.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
First of all, the problem you are experiencing has nothing to do with you having closed transition switches. Whether closed transition (make-before-break) or open transition (break-before-make) design, ATS's employ a feature called an in-phase monitor which is nothing more than a sync check circuit to only allow transfer when both sources are within a certain sync threshold (usually within 10 electrical degrees.) ....
I have never run across an open transition ATS that has a sync check. I have programed an extra delay on transfer from generator to utility to prevent possible issues with large motors that are running at the time of transfer.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Yes but that does not comply with the code wording stated in post #3 by Don.

How so? It doesn't seem to me like "timing the transfer" is part of the required test.

Anyhow, it seems like if there is an "emergency source available" light on the front of the ATS, measuring how long it takes for that light to come on after the test is initiated would tell you how long the delay would be. If actual power is lost, that's when it would transfer (unless there is an additional delay added into the ATS, but that delay could be added to the time it takes for the light to come on.)
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
How so? It doesn't seem to me like "timing the transfer" is part of the required test.

Anyhow, it seems like if there is an "emergency source available" light on the front of the ATS, measuring how long it takes for that light to come on after the test is initiated would tell you how long the delay would be. If actual power is lost, that's when it would transfer (unless there is an additional delay added into the ATS, but that delay could be added to the time it takes for the light to come on.)

the life safety and critical branches are automatically restored to operation within 10 seconds after interruption of the normal source.

Steve
What if the ATS fails internally preventing transfer to emergency.
My point is just because emergency power is available at the ATS doesn't mean it will transfer the load and restore operation.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Forgive me if this has been discussed before. I couldn't find it in a search.

I am in a healthcare setting and we are required to transfer power within 10 seconds which is tested monthly and documented. We can't always meet that due to our closed transition switches. Is there any exceptions to the 10 second rule that would allow for the syncing of the two power sources during testing? We could open normal power and will meet the time. However, there are many instances where it is not practical to do so.

When we go over, the timing is generally around 11-18 seconds. Any assistance would be appreciated. Thank you

While NFPA 110 8.4.6.1 says that the ATS must be operated electrically on monthly basis, I believe 8.4.6.2 gives you some relief on the timing. It indicates that an annual confirmation can be used for the timing issue. I think this was new to the 2013 edition.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Excuse me but I get a little annoyed when you spend the time to help and answer the OP with their questions and you get no response.
I understand there may be reasons for this. But are the monitors of these posts looking for these issues and taking measures to improve this forum?
Tks
 
Excuse me but I get a little annoyed when you spend the time to help and answer the OP with their questions and you get no response.
I understand there may be reasons for this. But are the monitors of these posts looking for these issues and taking measures to improve this forum?
Tks

I apologize for not responding sooner. I have been following the posts and researching while preparing for our JC survey.
I appreciate all of the responses and am calling out our Generator service company to check Frequency as well as other items that may not be allowing it to sync faster.


Thank you again!
 