  • jaggedben
    replied
    Originally posted by kwired View Post
    ... This is just an area for nit-pickers to dwell on when they can't find anything else to nit-pick.

    Leave a comment:


  • hbiss
    replied
    Agreed.

    -Hal

    Leave a comment:


  • kwired
    replied
    Originally posted by hbiss View Post
    I never expected there would be but some inspectors don't like that 1/4" or less between where it exits the siding and goes into the connector on the back of the panel. They say it's a wet location because water can get behind there.

    -Hal
    And some sort of enclosure to come out and into bottom of panel can get just as wet or even more wet than 1/4" or less into the back of a panel I would think. This is just an area for nit-pickers to dwell on when they can't find anything else to nit-pick.

    Leave a comment:


  • hbiss
    replied
    Originally posted by Dennis Alwon View Post
    I can tell you this- NC has had exterior panels for as long as I have been here and longer (1978) and there has never been an issue with the nm cable being inside the panels.
    I never expected there would be but some inspectors don't like that 1/4" or less between where it exits the siding and goes into the connector on the back of the panel. They say it's a wet location because water can get behind there.

    -Hal

    Leave a comment:


  • Dennis Alwon
    replied
    Originally posted by hbiss View Post
    As I recall, that's exactly the situation with coming into the back of an outdoor service panel on the side of the house with all the home runs. We talked about this before and I think some kind of wire enclosure under the panel was being used so that you would bring your wiring out, up and into the bottom of the panel instead of into the back and this thing would go over your wiring creating a dry location.

    I just recommended making outdoor service panels illegal.

    -Hal

    I can tell you this- NC has had exterior panels for as long as I have been here and longer (1978) and there has never been an issue with the nm cable being inside the panels.

    Leave a comment:


  • hbiss
    replied
    As I recall, that's exactly the situation with coming into the back of an outdoor service panel on the side of the house with all the home runs. We talked about this before and I think some kind of wire enclosure under the panel was being used so that you would bring your wiring out, up and into the bottom of the panel instead of into the back and this thing would go over your wiring creating a dry location.

    I just recommended making outdoor service panels illegal.

    -Hal

    Leave a comment:


  • Carultch
    replied
    Originally posted by augie47 View Post
    Don't give "them" and ideas
    The NEC specifically spells out the interior of a raceway in a wet location is considered a wet location. I do not believe there is any such reference to the interior of an enclosure in a wet location so an inspector would be hard pressed to give you a Code reference.

    Welcome !
    In the OP's situation, I would anticipate a small stub of raceway sleeveing the cable as it exits the building envelope and enters the disconnect enclosure. Would that small stub of raceway also qualify a "wet location", because it technically is a raceway in a wet location?

    Leave a comment:


  • jaggedben
    replied
    I would say that rules for wiring methods don't apply to the inside of enclosures, in general.

    The cable is a wiring method that gets from one enclosure to another. It could be a type of conduit instead. Either way, the rules for that wiring method stop when you get to the enclosures. When you bring the cable into the box and you remove the sheath and separate the conductors to land on various terminals, you are no longer using a cable as a wiring method. There are plenty of rules that apply to the enclosure, which take over. Just as if I bring conduit to a box, there are fill and derating rules that apply in the conduit and then as soon as the conductors enter the box those rules end and there are different rules for fill, etc.

    Leave a comment:


  • sanscow
    replied
    Originally posted by don_resqcapt19 View Post
    The 3R rating permits the inside of the enclosure below any live part to be wet and requires drain holes.
    So, would that mean the interior of the enclosure could be considered damp?

    Leave a comment:


  • kwired
    replied
    Originally posted by don_resqcapt19 View Post
    The 3R rating permits the inside of the enclosure below any live part to be wet and requires drain holes.
    Then they put entry hub in top center of the enclosure so that any raceway you connect to it will drain right onto any components you place in the enclosure

    Seen many main lugs and main breakers fail over years because of this.

    Leave a comment:


  • sanscow
    replied
    Originally posted by packersparky View Post
    I sure hope the interior of outside enclosures are not wet locations, or else millions of outside panelboards with breakers in them would be a violation.
    I think the manufacturers breakers are listed for use in both dry location and wet location rated enclosures.

    Interestingly enough, Eaton makes a series of interlocks that fit inside those same enclosures. One set it rated for indoor use and another set is rated for outdoor. This would suggest that even the manufacturer thinks the interior of their weatherproof enclosures is not dry a location.

    Pure logic would indicate that the interior of an outdoor enclosure is probably the most similar to the damp location definition and as such would violate 334.12(B)4 if wiring with Romex.

    Leave a comment:


  • don_resqcapt19
    replied
    The 3R rating permits the inside of the enclosure below any live part to be wet and requires drain holes.

    Leave a comment:


  • infinity
    replied
    The interior of a disconnect is not a wet location. It's that simple.

    Leave a comment:


  • ritelec
    replied
    Visiting a couple other forums a few years ago, others insisted that the wire has to be change to exterior rated wiring before going out to exterior receptacles, disconnects, lighting.. I never had issues in Jersey with Rx going to external boxes....... But then again, I see primary service conductors sleeved in schedule 40 pvc in areas subject to damage... (just to mention, I see a new service that went in, the electrician did this funky terrible looking bend at the service head on seu to make it perpendicular to the cable, but installs the schedule 40 in the driveway ???)

    Leave a comment:


  • packersparky
    replied
    Originally posted by augie47 View Post
    Don't give "them" and ideas
    The NEC specifically spells out the interior of a raceway in a wet location is considered a wet location. I do not believe there is any such reference to the interior of an enclosure in a wet location so an inspector would be hard pressed to give you a Code reference.

    Welcome !
    I sure hope the interior of outside enclosures are not wet locations, or else millions of outside panelboards with breakers in them would be a violation.

    Leave a comment: