The job: WA state, relocate the feed from the utility transformer to the existing water treatment plant transformer.
The system: Utility primary metering on a feed to a water treatment plant. After it leaves the utility's metering (isolation?) transformer the customer owned secondary is 12.5kV running ~4000' to a customer owned 12.5/7.2kv -> 208/120V transformer (112.5 kVA)
The problem: Contractor put in 2x 4" PVC and I don't think I can fit 3W+GND in just one conduit.
The question: Can you split one circuit across multiple conduits? It seems you can for low voltage in non-metallic conduits but what about MV cable?