Beat the elephant in the room (again!) about AFCI breakers...

Status
Not open for further replies.

sw_ross

Senior Member
Location
NoDak
This is more of a rant versus request for suggestions,

I did a basement finish out. I roughed it out last fall and put in some SP switches and some pigtail screw shells for the HO to have lighting for Sheetrock (they did it themselves). I had LED bulbs in the screw shells.

Everything worked fine all winter with no tripping issues on the lighting circuit.

I trimmed it out a couple days ago, using the LED 6" fixtures that resemble a can light 16 total. 2 bedrooms (4 each) and family room (8).

I had 2 dimmers in for the family room.

Now they're having arc fault tripping issues.

As an experiment I took out the dimmers and put the SP switches back in. Didn't help.

Last night he texted me to say that it tripped again, along with a circuit that feeds main level living room. That circuit has never tripped before! He had a hard time getting that circuit to reset. That breaker isn't located near my AFCI breaker in the panel.

I'll look at it today, but so much for making a profit on that project!
Frustrating! :rant:
 

growler

Senior Member
Location
Atlanta,GA
Everything worked fine all winter with no tripping issues on the lighting circuit.

I trimmed it out a couple days ago, using the LED 6" fixtures that resemble a can light 16 total. 2 bedrooms (4 each) and family room (8).

Are there any other loads on this lighting circuit ?

Also the Siemens has a self test function to see if the breaker is functioning properly. The breaker may be bad.
 

sw_ross

Senior Member
Location
NoDak
It shows AF on each of the trips.

The liv room circuit that trips is the older style that only has an indicator for AF.
The newt breakers I installed have AF and GF indicators.

The house isn’t that old (2014). The living room breaker that is now tripping is attributed to something I did... Even though I never touched the circuit!

I could change out the old breaker but the HO won’t pay for it since “I caused it”!
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
It shows AF on each of the trips.

The liv room circuit that trips is the older style that only has an indicator for AF.
The newt breakers I installed have AF and GF indicators.

The house isn’t that old (2014). The living room breaker that is now tripping is attributed to something I did... Even though I never touched the circuit!

I could change out the old breaker but the HO won’t pay for it since “I caused it”!
Of course! You're guilty!:roll:
 

growler

Senior Member
Location
Atlanta,GA
The house isn’t that old (2014). The living room breaker that is now tripping is attributed to something I did... Even though I never touched the circuit!

I could change out the old breaker but the HO won’t pay for it since “I caused it”!

Of course! You're guilty!:roll:

I had a service call a couple of years ago where an AFCI breaker was tripping and the home owner assumed it was the security company installers that had done something while installing the security system.

After checking things out I found that it was a new cable box that was causing the breaker to trip. I also figured out that it only tripped an older version breaker and so a new AFCI solved the problem.

My point here is that you may have to solve the problem to prove that it's not your fault and when you do then it's OK to charge them.

Change out the breaker and see if the problem goes away and if it does then bill for a service call. AFCI breakers go bad all the time so it's not uncommon.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I had a service call a couple of years ago where an AFCI breaker was tripping and the home owner assumed it was the security company installers that had done something while installing the security system.

After checking things out I found that it was a new cable box that was causing the breaker to trip. I also figured out that it only tripped an older version breaker and so a new AFCI solved the problem.

My point here is that you may have to solve the problem to prove that it's not your fault and when you do then it's OK to charge them.

Change out the breaker and see if the problem goes away and if it does then bill for a service call. AFCI breakers go bad all the time so it's not uncommon.

Was the new Cable box required for the security system?
 

sw_ross

Senior Member
Location
NoDak
They were normal length, 1 1/4” - 1 1/2”.
They hung the Sheetrock 2-3 months ago. It wasn’t until I put the permanent LED fixtures and dimmer switches that the tripping started.

I know there’s always a possibility that I’ve got a bare ground that is intermittently touching an exposed portion of a neutral. I’m not casting 100% of the blame on afci’s, but it’s just frustrating to have to deal with something that from the HO’s perspective “I caused”.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
They were normal length, 1 1/4” - 1 1/2”.
They hung the Sheetrock 2-3 months ago. It wasn’t until I put the permanent LED fixtures and dimmer switches that the tripping started.

I know there’s always a possibility that I’ve got a bare ground that is intermittently touching an exposed portion of a neutral. I’m not casting 100% of the blame on afci’s, but it’s just frustrating to have to deal with something that from the HO’s perspective “I caused”.

First use the diagnostic feature of the breaker to identify the kind of trip that occurred.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
After almost 20 years I would think they should have it right if there was any possibility of it being a viable concept.

-Hal

They would if AFCIs had the computing power, which would mean $165-$245 per breaker and a toasty panel.
 

sw_ross

Senior Member
Location
NoDak

Interesting. Have you completed the course?

It's sad that there has to be a course established on how to trouble shoot issues with AFCI breakers.

I'm interested/curious enough about the course content to spend a couple of hours doing it on a weekend.

Why is it that when I was an apprentice and AFCI's were only required in bedrooms (mid-2000's) we never had issues with AF tripping (that I can remember)?
Now that they're required everywhere issues with them are practically expected.
 