    The project is a renovation of existing office space. The spaces are becoming exam rooms. Many outlet devices are intended to be existing to remain. New devices are being served via hospital grade wiring methods and devices. Do the existing to remain devices require new hospital grade wiring methods and devices? Or can they remain as is (MC wiring methods).

    Electrical Design Engineer asking.

    #2
    If the rooms are now exam rooms any wiring that serves the receptacles must be HCF. So any old wiring and devices must be removed and replaced.

    -Hal

    Comment


      #3
      I believe only patient bed locations need hospital grade receptacles.

      Comment


        #4
        I believe that is correct

        -Hal

        Comment


          #5
          Thank you. The project is a smaller renovation area. We're directing the contractor to replace the wiring methods.

          Comment


            #6
            Originally posted by kgalle View Post
            Thank you. The project is a smaller renovation area. We're directing the contractor to replace the wiring methods.
            All patient care areas . This includes exam rooms, physical therapy and so on