And is no different than a MWBC with similar unbalanced current. L2 runs cooler, N runs a little warmer. Net effect of all three conductors in the raceway or cable is about the same - close enough NEC doesn't think we need to count all three as CCC's for ampacity adjustment reasons. If it were two conductors plus neutral of a wye system however, that current on the N is not unbalance current like it is with split single phase system. Maybe for a dryer it sort of wouldn't really make that much difference, but NEC doesn't single out this sort of thing as an exception to the rule.
But not to ignore the fact that there can be multiple current phases present and there may not be a true balancing out of currents. The NEC assumes loads are evenly split/balanced such that we get similar loading across lines. Any deviations are assumed to be ignorable.
Loading L1N and L2N with similar pf loads makes this assumption close. However, you could have something like a 30d lag (86.6% p.f.) on one line and unity on the other and that would give you 25.9% more current in the pipe than expected. Not such a small number considering that they count the neutral as a CCC for a 50% increase in current. The consequences of assumptions.