Is the neutral in 240v circuit a CCC?

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
IMHO, either the neutral is unused and does not carry current or it is part of an MWBC and is not counted. However an MWBC may not be strictly allowed to carry 240V line to line loads. The principle that any increase in neutral current must correspond to reduced current in one of the hots would still apply.

Sent from my XT1585 using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If it's from a 1Ø, 240 volt system then the neutral does not count as a CCC. If it's from a 3Ø, 208Y/120 volt system then it does count. Since you said 240 volts you're good. :cool:
 

kwired

Electron manager
Location
NE Nebraska
If it's from a 1Ø, 240 volt system then the neutral does not count as a CCC. If it's from a 3Ø, 208Y/120 volt system then it does count. Since you said 240 volts you're good. :cool:
I agree, same appliance generally can be used on either system and neutral will be a CCC if supplied from a wye system.
 

micabay

Appliance Tech
Location
Kitsap, WA
Occupation
Appliance Tech
Does your dryer have a 110 volts load?
If this is in the US of A, most dryers do. The motor, and computer is a 120vac load. The only load internal of the machine that is 240vac is the heater itself, which is typically around 5400 watts depending on brand. Some machines imported from overseas, such as Bosch or a lot of the 24 inch Apartment units, only use 240vac.
 

mivey

Senior Member
Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
Doesn't matter. As GoldDigger said above, any neutral current is current not being carried by a line conductor, so the neutral still need not be counted on 1ph.
 

kwired

Electron manager
Location
NE Nebraska
Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
If dryer needs a neutral connected then yes it does carry current. OP's question AFAIK is whether it needs counted as a CCC when it comes to ampacity adjustment purposes. On a 120/240 singe phase system, it only carries unbalanced current between the ungrounded conductors. In a wye system with only two of the phase conductors as the circuit, it doesn't carry imbalance current and has to be counted as a CCC for ampacity adjustment reasons.
 

mivey

Senior Member
Doesn't matter. As GoldDigger said above, any neutral current is current not being carried by a line conductor, so the neutral still need not be counted on 1ph.
You are correct of course. I had a complete mental lapse.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.

But then you would be sending current down the noddle and not the other hot leg.
 

kwired

Electron manager
Location
NE Nebraska
But then you would be sending current down the noddle and not the other hot leg.
And would still have same heating effects in a raceway or cable. L1 carries heater current plus motor current. L2 only carries heater current. N only carries motor current. (timer is sort of negligible amount of current and can be ignored here).
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
And would still have same heating effects in a raceway or cable. L1 carries heater current plus motor current. L2 only carries heater current. N only carries motor current. (timer is sort of negligible amount of current and can be ignored here).



Yes, but because that current is going down N and not L2, L2 runs cooler allowing for N to add heat without everything in the conduit getting too hot.
 

kwired

Electron manager
Location
NE Nebraska
Yes, but because that current is going down N and not L2, L2 runs cooler allowing for N to add heat without everything in the conduit getting too hot.
And is no different than a MWBC with similar unbalanced current. L2 runs cooler, N runs a little warmer. Net effect of all three conductors in the raceway or cable is about the same - close enough NEC doesn't think we need to count all three as CCC's for ampacity adjustment reasons. If it were two conductors plus neutral of a wye system however, that current on the N is not unbalance current like it is with split single phase system. Maybe for a dryer it sort of wouldn't really make that much difference, but NEC doesn't single out this sort of thing as an exception to the rule.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
And is no different than a MWBC with similar unbalanced current. L2 runs cooler, N runs a little warmer. Net effect of all three conductors in the raceway or cable is about the same - close enough NEC doesn't think we need to count all three as CCC's for ampacity adjustment reasons. If it were two conductors plus neutral of a wye system however, that current on the N is not unbalance current like it is with split single phase system. Maybe for a dryer it sort of wouldn't really make that much difference, but NEC doesn't single out this sort of thing as an exception to the rule.

Yes, yes and yes :)
 