Sub panels in commercial restrooms?

Status
Not open for further replies.

Muneepit

Muneepit
Location
Houston
Occupation
Electrician
Is a sub panel allowed in a commercial bathroom. I know the service disconnect cannot be, but what about an MLO sub panel?
 

Muneepit

Muneepit
Location
Houston
Occupation
Electrician
I personally don't see a problem other than it is an odd place to put a sub panel in a commercial building. But since space is a premium.......

I just wanted to be sure since the service disconnecting means is not allowed, I wasn't sure if it stated elsewhere in the code that sub panels, load centers etc shall not be installed in public restrooms.

Thank you for your response.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
240.24 is the section you need


(E) Not Located in Bathrooms. In dwelling units, dormitories,
and guest rooms or guest suites, overcurrent devices, other
than supplementary overcurrent protection, shall not be located
in bathrooms.
 

Muneepit

Muneepit
Location
Houston
Occupation
Electrician
240.24 would not apply to a restaurant or commercial kitchen, correct. Only dwellings, dorm.'s, guest rooms or guest suites.

I am bidding a kitchen addition to a restaurant that is showing a sub-panel in the employee restroom in the kitchen. I wouldn't put it there personally, but if that is where it is shown and as long as it does not contradict the code, then it should be ok.

I just wanted opinions from people smarter than me and know the code better than I do.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
well the accessibility issues w/commercial kitchens are compounded by what is often larger motorized equipment that does not accept loto....~RJ~
 