    House that I wired & power was turned on August of 2018. After 10 months, I received a call that the Homeline dual purpose AFCI/GFCI breakers (one to the dishwasher & one for the 3 island receptacles) were tripping.
    I just have a GFCI tester that I plugged in and things checked out, the breakers tripped when they were suppose to. I had the homeowners run the dishwasher from a separate circuit that the disposal was on & they said that the dishwasher ran through 2 uses OK.
    A LED, night light plug into the circuit that feeds the island receptacles, is the only thing (that I know about) that is being used on that circuit.
    Any suggestions?
    Thanks

    #2
    phone charger or laptop? put in new breakers? don't really know, just grasping at straws since you didn't get any replies
    Think for yourself, while its still somewhat legal!
    Clarkesville, Georgia

    Comment


      #3
      Anything electronic can mess with AFCI. Swap the dual function breaker with a straight GFCI breaker and see if it still trips. If it doesn't call Sq D and get some new breakers.
      If Billy Idol is on your playlist go reevaluate your life.

      Comment


        #4
        Originally posted by ActionDave View Post
        Anything electronic can mess with AFCI. Swap the dual function breaker with a straight GFCI breaker and see if it still trips. If it doesn't call Sq D and get some new breakers.
        It is in the county with no inspection, but, the state (Texas) is by the 2017 code, requiring AFCI/GFCI protection for kitchen area. Had tried my GFCI tester with 3 GFCI fault, & it held on all 3 receptacles. Must be an AFCI fault occurring like the previous post stated (LED & nigh sensing light).

        Comment


          #5
          I also suspect the night sensing light could be causing the AFCI breaker to trip. When the light is just on the threshold of switching near sunset it may be creating noise on the branch circuit which the breaker is misinterpreting as an arc. Years ago a friend of mine had a sensor activated light that interfered with neighbor's TVs near sunset, so they definitely can be noise generators.

          Comment


            #6
            Thanks one & all. I am tending to lean toward LED / electronics also. After 10 months, something.
            Years ago, young couple who had been in their house a month, called the general contractor that breaker for master bedroom was tripped. When he tried to reset it, sparks flew.
            Asked the builder to make sure everything was unplug-ed & then try it. Same results.
            Went out there, took panel cover off, no sign of sparks/arcing.
            Went to master bedroom, unplug-ed "new lamp". Circuit held! Plugged into dedicated circuit, breaker tripped!
            Charged service call.

            Comment


              #7
              I'm imaginging some sort of statistical analysis is being collected here>
              https://www.afcisafety.org/home-owne...nted-tripping/