    Garage wired via rx. in shmurf flex >>



    thoughts??
    ~RJ~

    #2
    Originally posted by romex jockey View Post
    Garage wired via rx. in shmurf flex >>
    thoughts??
    ~RJ~

    I don't see a problem with it. Since the runs are vertical they may not even need any sort of sleeve.
    The 95% of people that you can't trust give the other 5% a bad name.

    Comment


      #3
      It's a resi garage Growler, so rakes, shovels, etc ....i wuz thinkin' physical protection.....~RJ~

      Comment


        #4
        Here's what's permitted for protection of NM cable:

        334.15(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means.
        Smurf would need to fall under "other approved means" to meet the NEC.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          The title of that section is "exposed work". If you cover the cells involved with drywall or paneling or plywood, that would also be considered sufficient protection and may be less expensive to implement when the cables are already installed should the inspector reject the smurf solution.

          Comment


            #6
            Originally posted by infinity View Post
            Smurf would need to fall under "other approved means" to meet the NEC.
            Well, I approve. Does that count?
            Master Electrician
            Electrical Contractor
            Richmond, VA

            Comment


              #7
              Originally posted by romex jockey View Post
              It's a resi garage Growler, so rakes, shovels, etc ....i wuz thinkin' physical protection.....~RJ~

              Code wise requiring physical protection is about as ambiguous as it can get.

              There are inspectors that will turn this install down and others that would let it pass.
              The 95% of people that you can't trust give the other 5% a bad name.

              Comment


                #8
                I believe the crux of the question is whether the tube is not acceptable whereas the exposed NM would be. Does the use of the tube create a violation? I'd say no, it doesn't worsen the installation.
                Master Electrician
                Electrical Contractor
                Richmond, VA

                Comment


                  #9
                  Originally posted by LarryFine View Post
                  I believe the crux of the question is whether the tube is not acceptable whereas the exposed NM would be. Does the use of the tube create a violation? I'd say no, it doesn't worsen the installation.
                  I agree it doesn't make it worse. But does it make it better? As mentioned, 334.15(B) doesn't specifically say smurf is an approved means of protection. It's open to interpretation. I hate when things are open to interpretation. Interpretation costs me money.

                  ETA: Smurf is much more flimsy than schedule 40 and schedule 40 is apparently not an allowed method since schedule 80 was called out.

                  Comment


                    #10
                    Originally posted by Coppersmith View Post
                    Interpretation costs me money.
                    Kinda like having contact with the police. Every time it happens, it costs me time, freedom, money, or various combinations.

                    ETA: Smurf is much more flimsy than schedule 40 and schedule 40 is apparently not an allowed method since schedule 80 was called out.
                    Apparently sched 40 is looked at as being no tougher than NM, MC, or even EMT.
                    Master Electrician
                    Electrical Contractor
                    Richmond, VA

                    Comment


                      #11
                      Originally posted by Coppersmith View Post
                      I agree it doesn't make it worse. But does it make it better? As mentioned, 334.15(B) doesn't specifically say smurf is an approved means of protection. It's open to interpretation. I hate when things are open to interpretation. Interpretation costs me money.

                      ETA: Smurf is much more flimsy than schedule 40 and schedule 40 is apparently not an allowed method since schedule 80 was called out.

                      I to hate things that are open to interpretation.

                      If unfinished garages or unfinished basements require physical protection for wiring they could just come right out a say so. They could also state what level of protection.
                      The 95% of people that you can't trust give the other 5% a bad name.

                      Comment


                        #12
                        Originally posted by LarryFine View Post
                        Kinda like having contact with the police. Every time it happens, it costs me time, freedom, money, or various combinations.
                        Larry, I didn't take you for a frequent contact with police kinda guy. Are you revealing something?

                        Comment


                          #13
                          Type MC can be installed exposed. It would be a better choice for garages with exposed wiring. It's interesting to note that it's much more flimsy than the schedule 80 or rigid required to protect NM.

                          ETA: 330.12 says not allowed where subject to physical damage so I think I'm wrong about MC being allowed.

                          Comment


                            #14
                            Is the smurf supposed to terminate in a box? On the other end not shown. I was dinged, used greenfield (sleeve) to a water heater once in a basement; so pulled it out just left rx from floor joist to rx conn. on heater.

                            Comment


                              #15
                              Originally posted by sameguy View Post
                              Is the smurf supposed to terminate in a box?
                              In a complete raceway system, yes. As a sleeve, depends if the thing it's sleeving is properly terminated independent of the sleeve.