growler
Senior Member
- Location
- Atlanta,GA
What brand breaker?
I believe at one time you said you had Sq D Homeline. To diagnose one of those you reset the breaker, hold the breaker on, push the test button, if it trips in a micro second it's a ground fault, if it takes a little bit more time it's tripping on arc function.
Siemans has an trip window. GE has nothing.
I am doubtful of the self diagnosis feature and I am doubtful of AFCI technology so my method is to swap the breaker with a single purpose GFCI. If the breaker holds it's a nuisance trip. I have found that AFCIs will nuisance trip randomly with loads that have electronic components and your five year old fridge most certainly has those.
I think you need to reread the instructions on how to use the self diagnostics feature of a square D arc fault breaker.
I just looked it up and it says to turn the breaker off, hold the push to test button and turn the breaker on.
Immediate trip....ground fault
2 second trip.......arc fault
5 second trip.....short or thermal overload.