    HOT/NEU Reversal?

    Help me interpret this:

    3.0 volts green-to-white
    119.2 volts green-to-black
    120.9 volts white-to-black
    Sperry 5-light tester shows "HOT/NEU REV".

    House was probably built in the 1960s (?).
    3-wire plastic-jacketed NM cable, full-size ground wires.
    Plastic switch & receptacle boxes.
    100-amp circuit breaker panel.

    Click image for larger version

Name:	20190630-matt-GW.jpg
Views:	1
Size:	133.2 KB
ID:	2388927Click image for larger version

Name:	20190630-matt-GB.jpg
Views:	1
Size:	131.6 KB
ID:	2388928Click image for larger version

Name:	20190630-matt-WB.jpg
Views:	1
Size:	132.2 KB
ID:	2388929Click image for larger version

Name:	20190630-matt-HNR.jpg
Views:	1
Size:	135.0 KB
ID:	2388930

    #2
    Just this one receptacle, or all of them?

    Comment


      #3
      Have you tried the tester in a known good receptacle? Have you tried a different tester in that receptacle? Have you checked the wiring on that receptacle and at the distribution panel?

      Comment


        #4
        Originally posted by drcampbell View Post
        Help me interpret this:

        3.0 volts green-to-white
        119.2 volts green-to-black
        120.9 volts white-to-black
        Sperry 5-light tester shows "HOT/NEU REV".
        Since the neutral (white) and ground (green) are bonded in the panel you wouldn't expect to see a voltage between them. Since you are getting a little less voltage from hot (black) and green (ground) than from hot (black) and neutral (white).

        I would guess that there is a less than perfect connection on the ground path going back to the panel.

        If you use an extension cord plugged into a different good circuit you could measure using a different neutral and ground path.

        And you probably do have a hot and neutral reversed. I find them all the time after people change out receptacles.
        The 95% of people that you can't trust give the other 5% a bad name.

        Comment


          #5
          The 3V could be phantom voltage.

          Comment


            #6
            Was anything else running on that circuit at the time? How long is the circuit?
            Our comedian shamelessly joked about a blackout. Talk about dark humor.

            Comment


              #7
              I'd be looking for my>>>>



              ~RJ~

              Comment


                #8
                Originally posted by Jon456 View Post
                The 3V could be phantom voltage.
                Yes,

                Originally posted by romex jockey View Post
                I'd be looking for my>>>>



                ~RJ~
                but I don’t have one!

                OP, where did you find those ends for your DIY cable? I like it.

                Guessing you did not mess up on the cable, I’d say the polarity is correct. You may be measuring neutral VD dependent on the load on that circuit but am inclined to think the PV.

                The last option, reversal with a PP EG.

                Did I cover all the scenarios?
                Tom
                TBLO

                Comment


                  #9
                  I'm with growler.

                  Got a pic showing the wires and receptacle face at the same time?

                  Bring an extension cord from a good outlet on same leg and use it as a reference for measurements.
                  BB+/BB=?

                  Comment


                    #10
                    Small 1½-story bungalow, single-family detached.
                    Currently vacant, being prepped for sale. Absolutely nothing is plugged into any receptacle except the dishwasher & disposal. A few ceiling lights and the air conditioner were running at the time.

                    All of the receptacles on one circuit. (breakfast nook) Home run of maybe 30-40 feet, plus maybe 30 feet of cable interconnecting the four or five receptacles.
                    Every other receptacle in the house behaved as expected, but using only the Sperry tester and not following up with a voltmeter.

                    I did field-engineer an extension cord with the white & black deliberately reversed to see how the Sperry tester would respond, but succeeded only in tripping a GFCI. It didn't dawn on me to try it on another circuit (without a GFCI) until after I had returned home. I also plan to try a three-lamp neon-lamp tester, if I still have one and can find it.

                    Have not opened the panel to look.

                    I'm unconcerned about the three volts between white & green. If there's current flowing in the white and not in the green, there will be a little bit of voltage drop on the white and not on the green, and there will be a small voltage difference between the two.

                    Originally posted by Jon456 View Post
                    Have you tried the tester in a known good receptacle? ...
                    Is there any such thing? Even if I brought a new receptacle & breaker, and connected them to a panel with three short lengths of THWN -- out in the open where I could see each one -- I still wouldn't have 100% confidence that there wasn't a gremlin somewhere, such as a loose neutral at the meter or ground offset voltage in the Earth due to a multiply-grounded distribution network.

                    Comment


                      #11
                      Doesn"t matter about MGN.

                      If POCO neutral is at 2 volts to remote earth then the bond at the panel will make all of your grounds at 2 volts to remote earth. The neutral will be at 2 volts, excluding load voltage drop.
                      BB+/BB=?

                      Comment


                        #12
                        Originally posted by Jon456 View Post
                        The 3V could be phantom voltage.
                        Only if the EGC or bond is open. Possibly VD on neutral from another load. Hot/neutral reversal could be in termination to receptacle.

                        Sent from my XT1585 using Tapatalk

                        Comment


                          #13
                          Originally posted by GoldDigger View Post
                          Only if the EGC or bond is open. Possibly VD on neutral from another load. Hot/neutral reversal could be in termination to receptacle.

                          Sent from my XT1585 using Tapatalk
                          After a long day, sometimes the gold and silver screws look the same.
                          BB+/BB=?

                          Comment


                            #14
                            If there were truly a hot/neu reversal, you would have read around 120V from white to green.
                            I have one of those Sperry testers and got the same hot/neu reversal. I checked and there was no swapped wires anywhere. Turns out I had lost either a neutral or hot, can't remember.

                            OP, did you try a load on the receptacle? That would show if you lost part of the circuit.
                            If you aim at nothing, you will hit it every time!

                            Comment


                              #15
                              Originally posted by mivey View Post
                              I'm with growler.
                              Originally posted by Little Bill View Post
                              If there were truly a hot/neu reversal, you would have read around 120V from white to green.
                              Sorry Mivey but I think Bill is right and I was wrong.

                              Folks it was a little after 3 AM and some idiot had just called and woke me up and then I couldn't just go back to sleep so I thought I would mellow out by reading. I see now I didn't clearly understand the test made by Drcampbell .

                              The first thing I do when I get a reversed polarity reading is pull the receptacle and see if there is a black wire on the same side as the ground ( neutral should be on same side as ground if the light is poor and it's hard to tell difference between silver and gold).

                              In this case if the receptacle is wired correctly and no obvious faults such as bad back stab. Then go to the next receptacle in the daisy chain.

                              Good luck and I hope the bad wiring is in a junction box and not a flying splice in a wall.
                              The 95% of people that you can't trust give the other 5% a bad name.