    190718-2002 EDT

    If that was a 3 phase wye source, then wye line to line voltage would be about 193 V.

    .

    Comment


      #32
      It's 3 phase 120/208 but only single phase to the residence

      Sent from my SM-G965U using Tapatalk

      Comment


        #33
        Originally posted by ptonsparky View Post
        Now, what were the amperages on each phase?
        Is 116 a typo? Should be 216?
        Yes 216 sorry

        Sent from my SM-G965U using Tapatalk

        Comment


          #34
          190718-2313 EDT

          nickelec:

          Your measurements after correction do not correlate with a a center tapped single phase transformer with mostly resistive loading, and no major source series inductance.

          With whatever present loading is on my home I read 122.7, 122.0, and 244.7 . It is just luck that I didn't see a tenth or two difference in the sum. These measurements are with one meter, and power system voltage jumps around a little over short times.

          .

          Comment


            #35
            Originally posted by gar View Post
            190718-2002 EDT

            If that was a 3 phase wye source, then wye line to line voltage would be about 193 V.
            .
            Calculated using law of cosines with the 118V and 105V phases at 120 degrees from eachother?

            Comment


              #36
              Originally posted by nickelec View Post
              It's 3 phase 120/208 but only single phase to the residence

              Sent from my SM-G965U using Tapatalk
              But with the phase angle voltages don't add up with simple math like they do with true single phase 120/240 system.
              I live for today, I'm just a day behind.

              Comment


                #37
                190718-2351 EDT

                synchro:

                I used a different technique, but the result is the same.

                .