Announcement
Collapse
No announcement yet.
Grounding 4 square
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    Grounding 4 square
    If I am running #6 coper MC to a steel 4 square or 4-11/16 steel box for a range, how do I ground to the box?
    #2
    Since the EGC is solid a nut and bolt will do.
    Rob
    All responses based on the 2017 NEC unless otherwise noted
    Comment
      #3
      I think my MC is stranded, does the ground screw have to be green? Or an approved lug, I was wondering what other methods people are using.
      Comment
        #4
        Sorry you did say MC cable but I was thinking NM with a solid EGC. Yes you could just use a fork connector and a screw in the back of the box. There is no requirement that the screw has to be green.
        Rob
        Comment
          #5
          If I install the ground to the box how to I go to the receptacle, if I go to the receptacle how to I go to the box.
          Comment
            #6
            I believe the EGC inside #6 MC cable is # 10 solid. I've left it long enough to wrap around the ground screw and then to the receptacle.
            BTW, use the 4 11/16 box or a deep 4" square. You'll appreciate the extra space.
            Comment
              #7
              You pigtail it.
              Comment
                #8
                I didn’t know the ground was #10 in the mc it looked like #6 as well,if it is #10 I can see pig tailing it,
                Comment
                  #9
                  Depending on the cover you use you may not need a pigtail out to the receptacle, solid contact of mounting yoke to box/cover is sufficient. If you insist on a conductor to receptacle even if not required by code, then you need to find a method to pigtail it.
                  I live for today, I'm just a day behind.
                  Comment
                  Working...
                  X