    Single Phase 480 - 120/240V Transformer

    Does anyone see a problem with installing a SINGLE PHASE transformer (480V primary 120/240V secondary) fed from a 2-pole breaker from a 3-phase panel?

    #2
    Originally posted by MAster12 View Post
    Does anyone see a problem with installing a SINGLE PHASE transformer (480V primary 120/240V secondary) fed from a 2-pole breaker from a 3-phase panel?
    No, no problem at all. In fact, how else would you do it?
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

    I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.

    Comment


      #3
      Originally posted by Jraef View Post
      No, no problem at all. In fact, how else would you do it?
      Rob

      Moderator

      All responses based on the 2014 NEC unless otherwise noted

      Comment


        #4
        Depends on the supply voltage I suppose.

        Comment


          #5
          I think that what Jraef is saying is that if the primary is 1Ø, 480 volts you don't have much of a choice but to use a 2 pole breaker in the 3Ø panel.
          Rob

          Moderator

          All responses based on the 2014 NEC unless otherwise noted

          Comment


            #6
            Originally posted by infinity View Post
            I think that what Jraef is saying is that if the primary is 1Ø, 480 volts you don't have much of a choice but to use a 2 pole breaker in the 3Ø panel.
            You can use a three pole breaker but you ultimately only utilize two lines from the source.
            I live for today, I'm just a day behind.

            Comment


              #7
              Originally posted by kwired View Post
              You can use a three pole breaker but you ultimately only utilize two lines from the source.
              Very true but the OP did specifically ask about a 2 pole. I'm guessing that maybe he's concerned about an imbalance of some kind.
              Rob

              Moderator

              All responses based on the 2014 NEC unless otherwise noted

              Comment


                #8
                Originally posted by infinity View Post
                Very true but the OP did specifically ask about a 2 pole. I'm guessing that maybe he's concerned about an imbalance of some kind.
                Which is unavoidable other than to compensate by balancing any other single phase loads accordingly if possible.
                I live for today, I'm just a day behind.