I'm impatiently waiting for the Siemens wholesaler to call me back. Can any of you tell me if their Size 1 pump panels utilize the CT typpe overloads that I can loop my load wire through a couple times? Very few stock a Size 0 PP, Like none in this area.

I've done this with there starters years ago.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
When Siemens first bought out Furnas and started selling the Furnas Pump Panels, they would have definitely had the old Furnas ESP100 SSOL relays that were always CT based. But about 15 years ago they stopped selling the US made ESP100 and changed to the German version SSOL that they called the ESP200, bit it’s a totally different product design and I’m not sure if the smaller sizes still have the CT windows, I think they might be feed-through wiring IIRC.

The range of adjustment on the ESP200 was wider than before however, so you might be OK depending on what they are sending you.
 