3 years ago, I ran a circuit for an in ground septic pump. Recently this 20 amp, two pole, gfi breaker trips, causing water level to rise and sets off the alarm, etc. The customer has to go outside and reset it and it works ok for a week or month. Then trips again. My breaker is in a waterproof panel on a pole, with no sign of moisture inside. The septic person originally did all the underground wiring from my panel to the pump.
When I push the test button on the breaker, it tests fine. It doesn't matter if it's raining or dry weather. I will be asking the septic man to check his connections underground. That has to be where the problem is, correct ?
I wondered if changing the breaker to a regular non gfi would help. But I asked the local electrical inspector if the breaker needs to be gfi, she said yes, if its outside. Thank you for your thoughts.