RD35
Senior Member
- Location
- Bloomington, Indiana
Is there any reason, Code or otherwise, why I should not design a feeder system for a residence utilizing Aluminum Mobile Home Feeder cable in Sch 40 PVC that runs through the house from a 200A Service Breaker just inside the wall opposite the meter base to the MLO panel in the center of the home? The cable is compacted Aluminum with RHH, RHW-2, USE-2 rated insulation. Conduit will be suspended below the floor joists of the home and then run up into the bottom of the house panel. Terminations will utilize an anti-oxidation paste on the stripped ends of the compacted aluminum conductors and the lugs are CU/AL 75° rated. Size would be 4/0-4/0-2/0-4 for the 200A feeder.
Also, is there a code related reason, (or any other good reason) for why aluminum SER Cable is not available in 4/0-4/0-2/0-4 configuration?