lighting contactor wiring ?

Status
Not open for further replies.

jiml

Member
Tennis court lights outside:
Do you need to use a 2-pole lighting contactor when wiring lights that are 240v? Or, can you use 1-pole contactor and just tie the other leg to the breaker?
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: lighting contactor wiring ?

Please consider;

410.48 Double-Pole Switched Lampholders.
Where supplied by the ungrounded conductors of a circuit, the switching device of lampholders of the switched type shall simultaneously disconnect both conductors of the circuit.
 