    Tapping the secondary of transformer

    Greetings,

    Does the code allow for multiple circuits coming off the secondary side of a distribution transformer? We've got several circuits connecting to the low voltage terminals of a transformer and these secondaries would be protected by the mains of the panels they are feeding. Is this acceptable practice if the secondary terminals of the XFMR can accommodate multiple wires?

    Thanks,
    EE

    #2
    Sure. There are limitations
    240.21.B.3
    240.21.C
    Part VIII Supervised Industrial

    pick what fits