    Upside down meter base and disconnect

    Hello,
    we have a very narrow wall and the only 400 amp meter base / disconnect we can find with an 11-1/2” width is an overhead feed but we are under ground.
    The panel (Milbank M400-APS-BS) will be fully enclosed and not exposed to weather so I am not concerned with inverting the panel. That said I am concerned with the meter readout. Can you please tell us if we can install the panel upside down, yet have the meter read right side up?

    #2
    does the main breaker(s) operate vertically or horizontally? On must be up position if vertically.

    If you plug meter in "upside down", reading should decrease as energy is consumed.

    I live for today, I'm just a day behind.

    Comment


      #3
      Even if an inspector might approve this, most likely the POCO will not. They are used to terminating their wires in a certain spot and wouldn't want to have to look to make sure which way is right.
      If you aim at nothing, you will hit it every time!

      Comment


        #4
        Also the meter has to be listed for underground. A 400 amp meter/main for ug is bigger than what you have (the ones I've used) and has a barrier so your ug conductors can enter the bottom and terminate line side of meter and be isolated from load side conductors.

        Comment


          #5
          Originally posted by Little Bill View Post
          Even if an inspector might approve this, most likely the POCO will not. They are used to terminating their wires in a certain spot and wouldn't want to have to look to make sure which way is right.
          I agree.

          Roger
          Moderator

          Comment


            #6
            I cannot imagine that install being allowed. I would not pass it and I am certain the power company will not go for it. It looks like a disaster waiting to happen
            They say I shot a man named Gray and took his wife to Italy
            She inherited a million bucks and when she died it came to me
            I can't help it if I'm lucky

            Comment


              #7
              I thought most could go any direction. Here is one that would work. It is made by Milbank

              https://www.gordonelectricsupply.com...BoCerEQAvD_BwE


              Click image for larger version

Name:	MILBANE03938_WB_1_PE_001.jpg
Views:	183
Size:	8.7 KB
ID:	2530052
              They say I shot a man named Gray and took his wife to Italy
              She inherited a million bucks and when she died it came to me
              I can't help it if I'm lucky

              Comment


                #8
                Thank you all. Thought this might be odd and you confirmed. Given the narrow access we will go with a 400 amp pedestal which is 13” wide. Milbank U2849-0-2/200. We can mount in the wall. Believe it or not, every inch counts since we are between two concrete columns.

                Comment


                  #9
                  I can guarantee we wouldn’t set a meter in that installation. Too much potential for someone getting hurt while connecting, disconnecting meter.