2 pole breakers with tie bars

Status
Not open for further replies.

jwolchko

New User
Location
Virginia, USA
I've run into something I've never seen before...
I'm looking at a 3 phase panel with three two pole breakers that are all tied together to feed a sub-panel. I haven't pulled the cover off, I don't have arc flash gear. I need to add another sub-panel to this panel and am trying to figure out what's going on so the I can make a panel schedule and one-line to put in the construction drawings. Why not just put in a single 3 pole 124 Amp breaker? What is the purpose of this?

Just wondering if anyone has seen anything like this and could help me with it. Thanks.

Picture of this on my Google Drive https://drive.google.com/file/d/1Ce-wrt6_z0IAxvmhSKTWxcHucTARDZaF/view?usp=sharing
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Unless the breaker manufacturer provides it as a tested unit, paralleling of breakers (without a common trip) is not allowed. But if this is just using two poles of each breaker to feed one ungrounded conductor it might be allowed.
Two three-pole breakers with a handle tie would not be allowed for sure.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looks like listed Square D breaker:

998420-portrait_ratio1x1-300-300-be35374ce12313e74bc87c3558a62e70-WU.jpg


https://www.graybar.com/store/en/gb/qob-circuit-breaker-high-interrupting-capacity-89034885#{Mounting%20Type:Bolt%20On%20Mount}&{Interrupting%20Rating:22kA}&{Amps:125A}&{Voltage%20(Volts):120/240%20Vac}&{Brand%20or%20Series:QOB}&{Poles:3-Pole}
 

jwolchko

New User
Location
Virginia, USA
Looks like listed Square D breaker:

998420-portrait_ratio1x1-300-300-be35374ce12313e74bc87c3558a62e70-WU.jpg


https://www.graybar.com/store/en/gb/qob-circuit-breaker-high-interrupting-capacity-89034885#{Mounting%20Type:Bolt%20On%20Mount}&{Interrupting%20Rating:22kA}&{Amps:125A}&{Voltage%20(Volts):120/240%20Vac}&{Brand%20or%20Series:QOB}&{Poles:3-Pole}

OK, Make sense now. It deceived me to think it was something else. THANKS!
 

jwolchko

New User
Location
Virginia, USA
I see now that I wasn't paying attention to the fact that only one of the 2 pole modules was branded and the other two are blank. Feeling embarrassed...
 