Using nipple between meter socket and disconnect

Status
Not open for further replies.

Dansos

Senior Member
Location
PA
We are installing a 200A meter socket directly on top of an existing 200A disconnect. I plan on using a 3” galv close nipple to run the wires through. If the top of the disconnect has a hub knockout on top of it, is a hub required for the nipple to thread into? I wanted to have the meter socket almost directly on top of the disconnect so it will be within PoCo’s height requirements... I know 2-3” isn’t gonna make or break this but I just want to know if using a hub is REQUIRED by NEC for this application.
Thank you
 

Dansos

Senior Member
Location
PA
PS the meter socket will be fastened to the building with strut. It will not be “resting” on the disconnect in any way
 

Dansos

Senior Member
Location
PA
Thank you. I guess I figured the meter would be so close to the disconnect it wouldn’t matter but now I see your point.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You need something beyond a standard locknut. If there are no concentric or eccentric KO's you can use a single sealing locknut as electrofelon suggested with a close nipple.
 