When derating for conduit fill at 4-6 ccc at 80%,does it matter if 2 conductors are running different amperage than the other 4 conductors. I have one circuit 30 amp and two others at 20. The 30s are on #10 and the 20s are on #12 after proper derating,
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No it doesn't matter all you are doing to adjusting the actual ampacity of the conductors. If you have 90° C conductors like THHN then the #10's are good for 32 amps after derating and the #12's are good for 24 amps. If after the adjustment they are too small you would need larger conductors.
 