    Anyone know if you can legally cover a flex to EMT transition? Using a rated fitting of course.
    What do they mean in 300.15 requiring a box or or conduit body for other listed items including a "switch point"? What is a "switch point" in this code as I can find no explanation? Are they saying transition from one conduit system to another? "Outlet" is already listed so I do not believe they mean a wall switch as outlet covers that.
    300.15(F) says a fitting must be left exposed if used in lieu of a box or conduit body.
    I cannot determine if I am required to use a box or conduit body and am instead using a fitting in lieu of them as allowed. But then it may be required to be accessible.
    This is confusing so hopefully someone smarter than me can help.
    Thanks!!
    #2
    You need to look at Art 348. The key here is it a straight adapter as opposed to an angle or 90 degree. A straight adapter can be concealed. See 348.42.
    Comment
      #3
      I cannot determine if I am required to use a box or conduit body and am using a fitting in lieu of them witch would mean I must not cover it.
      I don't see how that section specifically addresses a transition from one wiring method to another.
      Rob
      All responses based on the 2017 NEC unless otherwise noted
      Comment
        #4
        My question was not with angled or straight connectors. Thank you for the article, I did read it again.
        Comment
          #5
          I believe it is the section that states where a box or conduit body needs to be installed. It lists examples of when they are and are not required. Please direct me to the more appropriate section if you could. I could be totally lost. Thank you
          Comment
            #6
            Yes, I think I understand you in that you are using a listed transition fitting. Same as a connector in this context. In my view 348.42 allows this.
            In the old days we used to use a rigid coupling, SS connector and a straight flex connector cobbled together. Never really compliant but that was before transition adaptors were available.
            Comment
              #7
              IMO, I think 300.15(F) applies to your install.
              Comment
                #8
                One thing to which I pay attention when using flex is which end should get the outside end of the spiral, which most fittings grip better. In a case where one end is more likely to be stressed, or as in this case will be rendered inaccessible, the outside end should be oriented toward that end of the run.
                Master Electrician
                Electrical Contractor
                Richmond, VA
                Comment
                  #9
                  A note about the origin of rule 300.15(F):
                  https://neca-neis.org/code-question-.../cqd-5-29-2017
                  Comment
                    #10
                    That's kind of similar but that is for a transition from a cable to a raceway where you would typically use a box not a raceway to raceway transition where a box isn't required.
                    Rob
                    Comment
                      #11
                      300.15 makes sense, you need to have access where wires might get jammed up in a transition.
                      But, I never understood why it's alowed to use flex in concealed locations.
                      To me, trying to fish wires through concealed flex with bends is almost as bad as going through an other than straight fitting.
                      John,