Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
the inspector says we need two outlets if the bath vanity has two sinks. True ? I wish he would’ve seen this in the rough in inspection. Thank you
the inspector says we need two outlets if the bath vanity has two sinks. True ? I wish he would’ve seen this in the rough in inspection. Thank you
210.52(D) Bathrooms. At least one receptacleoutlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge ofeach basin.
Do you have no more than the maximum of 3' that Tom mentioned? Here's the code wording, sounds like one duplex will be complaint.
I wish he would’ve seen this in the rough in inspection. Thank you
A single receptacle may serve two sinks as long as it's close enough to both, as in being between them.
A single receptacle may serve two sinks as long as it's close enough to both, as in being between them.
That would be one long vanity.Just to clarify, a single bowl vanity 36' long only needs one outlet, right ?
Just to clarify, a single bowl vanity 36' long only needs one outlet, right ?
oops, yes you are correct, my mistake 36"That is correct but it must be with 30" of the sink even if you had a 36' long vanity--LOL.. I assume you meant 36"