Transformer Question

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Personally if the transformer info does not state that you can step up or down then why do it. I doubt it would be compliant based on the listing.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Personally if the transformer info does not state that you can step up or down then why do it. I doubt it would be compliant based on the listing.

I don't even know the use for the tranny. Just got a text from a friend with pics of the tranny. I was just wondering if it could be reversed. I'm sure they will ask since they asked me to call, which I haven't yet.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Well, I came to the wrong conclusion in assuming they would ask if it could be reverse wired. That's usually the type thing they would ask but not this time. They only wanted to know if it would work for 277V stepped down to 120V. The wiring diagram confused them. I told them how to wire for 120V secondary. But what I didn't tell them was the OCPD. The load is only LED lighting so I think a 15A OCPD would suffice, is that correct? Also, would just the primary need OCPD or would both it and the secondary need it?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
This thread got me looking at Table 450.3.B, for small transformers. This transformer in question is a good example:
277V/120V, 1KVA
primary 3.6A
Secondary 8.3A​

Primary only protection, currents less than 9A, Maximum rating is 167% x 3.6 = 6A No provision for Next Size Up

Primary and Secondary Protection,
Primary Maximum rating is 250% x 3.6 = 9A.
Secondary, currents less than 9A, 167% x 8.3 = 13.9A.
Again, no provision for NSU.​


I am baffled for a couple of reasons;
1. How come I never noticed this before? :?:dunce: I checked back three cycles - no change. I don't recall ever working a small transformer before - unless it was in a control panel. I would have used primary and secondary fuse for that .

2. So what are they telling us - Use fuses? That doesn't seem reasonable.

So why don't I use 240.4.B, NSU for CBs 800A or less. T450.3.B has provision for NSU for currents 9A or more. So, I thinking they would have included the NSU if they thought it was necessary.

Anybody got any clues where I am missing the point?

Color me a confused