Two 750's and one 350 in 3" pvc/rigid. Two 90's(that I know of), 150 feet long, existing conduit under parking lot and concrete slab.
Can I do it or am I doomed to fail? Conduit fill ratio works, but jamming is the concern. Only ever put 750's in 4 inch.
I need more than a 400 amp single phase service according to a quick manual load calc. Thinking about getting to 475 amps with the 750's wire ampacity and then using the round up rule to allow a 500 amp main breaker or use a combination of service disconnects/panelboards. Haven't decided yet, just trying to figure out if the wire size in the conduit will work to get the ampacity I need.
Thanks for the help.
Can I do it or am I doomed to fail? Conduit fill ratio works, but jamming is the concern. Only ever put 750's in 4 inch.
I need more than a 400 amp single phase service according to a quick manual load calc. Thinking about getting to 475 amps with the 750's wire ampacity and then using the round up rule to allow a 500 amp main breaker or use a combination of service disconnects/panelboards. Haven't decided yet, just trying to figure out if the wire size in the conduit will work to get the ampacity I need.