brianthejabroni2
Member
so I was wondering I have (6) 20 amp single pole circuits I’m trying to run in one conduit. If I upsize my wire to #10 can put all 6 circuits in that 1 inch emt pipe ? When I Derate I go to the derating adjustments go under 10 to 20 and see multiplier is .50 .... 75 degree Column for #10 is 35 amps which means I get 17.5 amps derating but that’s where I get confused