Disconnecting means for a unit heater

Status
Not open for further replies.

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
I am wiring a gas unit heater, The breaker is about 50' away in-site. I plan on putting a switch right next to it about 3' away. The heater will be 15' in the air. Does that meet the disconnecting means for a unit heater installation?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
50' or less away and the circuit breaker will qualify as the disconnecting means. You can add one next to the unit if you want.
 