LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
Hello~

Does a 480/277 volt main disconnect need a neutral run with the ungrounded conductors for ground fault protection?

Note: The disconnect in question contains a black wire run with the ungrounded wires that is marked with green tape. The conductor is attached to the service bonding locknut, and then it is attached to the metal case. I believe the conductor serves as the equipment grounding conductor.

After considering the bonding and grounding DVD's, I believe that the service needs a neutral. Am I thinking correctly? If answered, then I'll share the results with my electrical students.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Hello~

Does a 480/277 volt main disconnect need a neutral run with the ungrounded conductors for ground fault protection?

Yes, the neutral must land in the main disconnect, which is where the premises EGC and GES conductors join it.
 

Russs57

Senior Member
Location
Miami, Florida, USA
Occupation
Maintenance Engineer
IMHO, you are asking two different things.

Ground fault protection doesn't require a neutral or a ground to work correctly.

A POCO service disconnect needs a neutral, and a ground, and they need to be bonded together at this location and only this location.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMHO, you are asking two different things.

Ground fault protection doesn't require a neutral or a ground to work correctly.

A POCO service disconnect needs a neutral, and a ground, and they need to be bonded together at this location and only this location.

Where does the "ground" come from?
 
IMHO, you are asking two different things.

Ground fault protection doesn't require a neutral or a ground to work correctly.

A POCO service disconnect needs a neutral, and a ground, and they need to be bonded together at this location and only this location.

It doesnt necessarily need a neutral. We need to know if this is a grounded system.
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
Yes, the 3 phase disconnect is the main service.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If this is a 480Y/277 volt service then a neutral must be brought to the service disconnect. It should be identified according to Article 200 and should not be green.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Since it is the Main Service Disconnect see 250.24(C)

Roger
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
Since it is the Main Service Disconnect see 250.24(C)

Roger

Hello:

That's the way I read 250.24 (c), but some say that the type of load matters.

On the contrary, I think that the neutral needs to run to the service disconnecting means to provide a low impedance path back to the transformer for clearing ground faults. Therefore, the type of load is not a factor.

Indeed, in this situation, one questions if a fault occurred, then would the fuse ever blow?

Best,

Diana
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
Here is a pic of the disconnect. Of course, the make-shift fuses are bizarre as is the absent GEC and electrode.
 

Attachments

  • IMG_0814.jpg
    IMG_0814.jpg
    91.8 KB · Views: 8

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Hello:

That's the way I read 250.24 (c), but some say that the type of load matters.
They are wrong, it only depends on whether it's a grounded or ungrounded supply.

On the contrary, I think that the neutral needs to run to the service disconnecting means to provide a low impedance path back to the transformer for clearing ground faults. Therefore, the type of load is not a factor.
You've got it except "ground" should be removed before faults.

Indeed, in this situation, one questions if a fault occurred, then would the fuse ever blow?
Not with out the neutral which serves dual purposes at the service equipment.

Best,

Diana

Roger
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
They are wrong, it only depends on whether it's a grounded or ungrounded supply.

You've got it except "ground" should be removed before faults.

Not with out the neutral which serves dual purposes at the service equipment.



Roger

Ok, I feel better about asking my administers to ban the use of the equipment until the disconnect is redesigned and appropriately installed. Thank you.
Best regards,
Diana
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Ok, I feel better about asking my administers to ban the use of the equipment until the disconnect is redesigned and appropriately installed. Thank you.
Best regards,
Diana

As already pointed out by others, if this is a grounded service then the neutral must be brought to the service disconnect in a compliant manner. The fact that the load does not require a neutral is irrelevant as you know for fault return path.
That conductor you mention that is marked as an EGC is of interest. Do you know where it connects at the other end? If it is connected to the POCO transformer X0 terminal you may have a fault return path, just not a technically compliant one. To be compliant the conductor should be marked white and terminate in a proper neutral bar in the service disconnect and have a proper main bonding jumper. Also, I don't see any evidence of a GES.
 

Awg-Dawg

Senior Member
Location
Dayton Ohio
Is it possible it’s a privately owned transformer and not a utility owned?

Or maybe even another disconnect grouped at another location?
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
The transformer is utility owned, and the disconnect is the main service. Good question though.

In the end, Roger made clear the issue and Article 250.24 (c). Thank you for taking the time to respond.

Best,

Diana
 