Ok Guys and Gals, I have a Sub Panel question. 320 amp service, one panel is just a 200 amp main with empty load lugs. I have a barn approx 300 ft away from the home (and the main service) I have 330 ft of 4/0 4/0 2/0 4awg quadplex aluminum wire. What is the largest sub panel I can install in the barn?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Hmmm, sounds like a homework question, give us your answer and how you arrived at it and then someone can critique your answer.

Roger
 
Ok Guys and Gals, I have a Sub Panel question. 320 amp service, one panel is just a 200 amp main with empty load lugs. I have a barn approx 300 ft away from the home (and the main service) I have 330 ft of 4/0 4/0 2/0 4awg quadplex aluminum wire. What is the largest sub panel I can install in the barn?

The largest panelboard you can install is 1200 amps. That is as large as they get. Ok, more details required. Is the run to the barn a set of service entrance conductors installed per 230.40 exception #3? Thats what I would do, less equipment and less wire but since you speak of a 4th wire, then maybe this is a feeder?
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
Ok Guys and Gals, I have a Sub Panel question. 320 amp service, one panel is just a 200 amp main with empty load lugs. I have a barn approx 300 ft away from the home (and the main service) I have 330 ft of 4/0 4/0 2/0 4awg quadplex aluminum wire. What is the largest sub panel I can install in the barn?

4/0 aluminum is good for 180amps @75C so that's what you have unless you have to derate for temperature. @60C it's 150 amp. It's a feeder not a service so you can't run it at 200 amps
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
4/0 aluminum is good for 180amps @75C so that's what you have unless you have to derate for temperature. @60C it's 150 amp. It's a feeder not a service so you can't run it at 200 amps
Being a feeder vs a service has no bearing on whether you can use the table for dwellings in order to use a lesser AWG conductor. The rule is for service or feeders that serve the entire load. If you have a disconnect outside that just feeds the inside panel, the conductors from the disc to the panel are feeders. If the inside panel serves the whole house, then you can use reduced the AWG according to the table even though they are feeders.

This reply has nothing to do with the OP's question or situation.
 
Last edited:

tom baker

First Chief Moderator
Staff member
Your question is not correct, largest subpanel could mean size. 180 amp feeder breaker to what ever size panel you want.
Now the 300 ft is another issue altogether. You would need to determine what 3% volt drop results in at 180 amps, if VD is excessive then back down on the size of the feeder breaker
 

Frank DuVal

Senior Member
Location
Fredericksburg, VA 21 Hours from Winged Horses wi
Occupation
Electrical Contractor, Electrical Engineer
Lots of online voltage drop calculators. Use two of them and see what they say!

Voltage drop is clearly the determining factor of amps useable at this distance. The voltage drop will limit the feeder size before the wire does using any table.:thumbsup:
 

izak

Senior Member
Location
Springfield, MO
You can use a large a panel as You want.
Someone pointed out to make sure the lugs in the panel that You choose are large enough for the wire.
Size the feeder breaker to protect the wire.
Voltage drop calcs wont require You to put in a smaller breaker; it is a suggestion.
 

swptln

Member
Being a feeder vs a service has no bearing on whether you can use the table for dwellings in order to use a lesser AWG conductor. The rule is for service or feeders that serve the entire load. If you have a disconnect outside that just feeds the inside panel, the conductors from the disc to the panel are feeders. If the inside panel serves the whole house, then you can use reduced the AWG according to the table even though they are feeders.

This reply has nothing to do with the OP's question or situation.

310.15(B)(7) is not applicable here, it's a feeder for a barn, not a dwelling. Just as a note as well, Quad-plex is not rated to be run inside a build or structure.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
310.15(B)(7) is not applicable here, it's a feeder for a barn, not a dwelling. Just as a note as well, Quad-plex is not rated to be run inside a build or structure.

If you read the last line in my post you will see that my reply didn't apply to the OP's situation since it was a barn.
I was replying to Eddie702, explaining there is no difference between a feeder and service as far as 310.15(B)(7) is concerned.
 
310.15(B)(7) is not applicable here, it's a feeder for a barn, not a dwelling. Just as a note as well, Quad-plex is not rated to be run inside a build or structure.

It depends on the specifics of the quad. If it is just use-2 then true. Often the quad I get is use-2/rhh-2 which is ok inside. "Quad", "4 wire URD", "mobile home feeder" are rather general terms with the insulation type varying by manufacturer.
 