Have a customer telling me he is having multiple arcfault breakers trip at the same time. The service is brand new. 400 amp 320 continous underground with a pedestal meter. Two 200 amp main panels in the basement with two 100 amp sub panels located different parts of the home. He’s finding tripped arcfault in all four panels at the same time. I’m at a loss. This has now happened three times since he moved in end of August
Announcement
Collapse
No announcement yet.
Arc fault breakers tripping
Collapse
X
Originally posted by Hv&Lv View PostOld brushed vacuum cleaner? What’s he trying to use when this happens? All four trip at once when he does what?
It once took me several trips and basically a camp out with customer to eventually discover that a flat screen tv when the screen would go bright white during a commercial would trip random breakers. Even arc faults not associated to that particular circuit.
Have Fun figuring it out.
Comment
Originally posted by mopowr steve View Post
Doesn’t have to be old, I had a customer, new house, new vacuum but this vacuum had 2 motors (one for suction and one for beater bar) whenever the second motor was turned on arc fault would trip.
Pit didn’t trip more than one though..
Comment
First time this happened no one was home next two times was sometime during the night. He discovered the problem when he woke the next morning. We’re talking dozens of arcfault breakers. The other thing it’s only arcfault style that are tripped. GFCI and standard single and double pole are fine
Comment
Who is the manufacturer of the breakers? Does he live near a radio, TV or cell site? Any 2-way radios being used? You say they are new, have you contacted the manufacturer to see if they are the latest version?
Any UFOs?
-Hal
Comment
This is another case where the breaker manufacture should be responsible for figuring out the issue and covering any costs to correct it unless they can prove its a wiring issue.
OP....you might want to get the date codes off the breakers and call the manufacture to see if there are any know issues.
A number of years ago I had 2 customers call me stating all the AFCI breakers we had just installed were tripping a once a week. I called Square D with the dated codes and said I was having problems at 2 new homes with all AFCI breakers tripping intermittently. The support person immediately asked if they were tripping once a week and I responded yes! He said that it was a know issue within a certain date range. He said I need to replace the breakers. I asked if there was a recall similar to the one they had a few years prior and he said no. They only informed people if they called about the issue. I personally think this is total BS. How may hours did other electricians spend troubleshooting or just replacing the AFCI's with standard breakers?Curt Swartz
Electrical Contractor
Comment
One way i troubleshoot a AFCI in residential is by installing a GFCI breaker and turning on every light, fan or other load in the home, or just leave it there for a weekend.
I plan to get a Siemens QE115 tor troubleshooting random tripping AFCI's: https://mall.industry.siemens.com/ma...mlfb=US2:QE115
If you have a 30ma ground fault something is really amiss.
For example last week I was brought into a service call that had an fellow electrician stumped they had "1 or 2 AFCI breakers tripping". They were going over radio interference, looking at vacuums etc. Turns out the house roper had run a 14/2 down a hall for a 3-way traveler and was using a neutral from the other lighting circuit in a light box.
Hope this helps
CheersComments based on 2017 NEC unless otherwise noted.
Comment
Similar problem about a year ago with a friend. He is in the public safety field and carries a Motorola trunked radio home each night and many nights left it on but muted for alerting. In certain locations, if the radio would transmit, several AFC breakers would trip from the RF interference. He wasn’t transmitting, just the radio would briefly affiliate with the towers.
Finally saw the red transmit light on the radio sync with a trip.
Comment
Originally posted by tortuga View PostOne way i troubleshoot a AFCI in residential is by installing a GFCI breaker and turning on every light, fan or other load in the home, or just leave it there for a weekend.
Hope this helps
Cheers
-Hal
Comment
There are a lot of good ideas.
Iwould start with this.
If it's the same breakers that trip every time, I would swap out those breakers with others that haven't tripped in the house and see what happens.
Comment
With it that spread out, I would look into a main neutral issue, that would be a common link. I wouldn’t think it would be an improper neutral to ground bond at each panel causing it, but it’s worth a look. I had one house the utility company forgot to tighten the neutral at the transformer.
Comment
A suggestion is to ask customer to note down which breakers tripped in what panel, if he is willing and reasonably competent. That way you could see whether all or at least most of the tripped breakers are one phase. If so, there might be a loose connection on that phase causing the problem.
Based on my limited understanding of AFCIs I don't think they have much discrimination of load vs line side problems compared to GFCIs, which measure unbalanced currents on the load hot and neutral conductors. So if there's more than a 5 amp load on an AFCI breaker and a sufficiently large noise voltage above 100 KHz on the bus due to arcing or something else, this would modulate the current out of the AFCI and perhaps trigger the series arc detection and trip the breaker. At least that's my theory.
Comment
Comment